Sparkingchip:
The test results sheets ask for the rating of the RCD IΔn mA and the disconnection time in mS.
That is what you need to record, it is the 5Δn disconnection time test result that you don’t need to record on the certificates.
Andy B
That can't be true if the RCD is used for ADS in most final circuits TT systems where the circuit requires a disconnection time of 0.2 s, and the RCD trip time exceeds 0.2 s - as it doesn't verify ADS. Even if the 1x test is below 0.2 s, it doesn't mean the 2x test or 5x test would pass.
It's also not true where a 10 mA or 30 mA RCD provides Additional Protection, as the required test is "at least 5x".
Therefore, more often than not, the 5x trip time value is required for verification as per BS 7671 requirements.
Sparkingchip:
If you were required to record the X5 test result it would ask for it. Have a look at section 11 of the IET OSG.
Yes, 11.5 - Additional protection - requires x5 test. QED.
Agreed that where a BS 4293 RCD only provides ADS in TT systems, 11.2 x1 test may be acceptable, but if it provides additional protection, 11.5 applies also.
Following only Section 11.3 would not necessarily verify ADS in TT systems (but would be OK for TN systems) - as I've discussed the x5 test is required because we don't have a x2 test and I'm not (personally) satisfied that passing the x1 test is OK, as I've had x5 with longer trip times than the x1 test.
Section 11.4 is unlikely to apply, as regardless of the debate on whether BS 7288 is accepted in 18th Edition, for the following reasons:
as I've discussed the x5 test is required because we don't have a x2 test and I'm not (personally) satisfied that passing the x1 test is OK, as I've had x5 with longer trip times than the x1 test.