Obviously in my diagram the circuit protective conductor (earth wire) in the cable supplying the faulty immersion heater should have stopped the cylinder, pipes and tap becoming live
the touch voltage during a fault is reduced to a maximum of 50 Volts
411.3.1.2 Protective equipotential bonding
...main protective bonding conductors... shall connect to the main earthing terminal extraneous-conductive-parts including the following:
(i)Water installation pipes
(ii) Gas installation pipes
(iii) Other installation pipe work and ducting
(iv) Central heating and air conditioning systems
(v) Exposed metallic structural parts of the building
Ian2304:
My lack of actual experience is clearly telling. Thank you for spending some time elucidating matters for me.
There are people on this forum who have written books on the subject, once you have grasped the basic issue there are literally chapter and verse written on the subject to read.
geoffsd:
With RCDs fitted the 200A can be discounted as the current required to operate the RCD is only 30mA, so the impedance can be 1,666 Ohms (50 / 0.03). Were the impedance to be above this 1,666 Ohms then SB would still be required but this is very unlikely.
Yes but the RCD doesn't limit the shock current to 30 mA. What it does do is limit the duration to 40 ms at 150 mA or greater.