ebee:
Chaps,
I would hope you`d ask why they`d want an EICR before commencing.
Evidence of poor previous work or just contentment of knowing it is satisfactory. That would decide whether you might make free minor corrections without referring back to them
Absolutely. If I take out a fuse from a switched fused connection unit supplying a gas boiler system that should be a 3 Amp size, but find a 13 Amp fuse instead, I change it there and then. It is easier to put the correct size fuse back than do more paperwork. Then I do not have to worry about that again. I have also done that with fuse wire as well in older installations. Who wouldn't? Tight time constraints cause cut corners.
"Where an observation requires further investigation (FI) because the inspection has revealed an apparent deficiency which could not, owing to the extent or limitations of the inspection, be fully identified and further investigation MAY reveal a C1 or C2 item, this should be recorded within section K, given the code F1 and marked as unsatisfactory in Section E." P. 475 B.S. 7671.
If we are to assume guilty until proven innocent, then FI should be done away with and a C2 used in its place. FI causes confusion and is an unnecessary duplication.
Z.
ebee:
Sorry Zoom I do not agree.
Where a genuine F1 applies it could be something that is a C1 or a C2 lurking there and as such we`d condem.
However it could be a C3 or even no code at all.
Until it is investigated and therefore determined we must make it condemable. We can`t give it a pass (yet) or a fail (yet) we can only record a potential unsatisfactory as a (assumed) unstisfactory. Therefore F1 unstaisfactory
An F.I. means that we have not completed our job. It is a cop out, get out of jail free card. If we can not gain access to a locked room we report so. We do not put F.I. and then condemn the installation. We can't report on don't knows. The report can't be completed until we do gain access to the locked room and its electrics.
The report is not complete until the work is finished. In this case the work of inspection and testing.
If the customer asks why an installation has "failed" he won't be happy because we say further investigation is required. He has a right to say: "Well get on with it then".
Dave Stone would not disconnect a cable where it could not be identified as to its use or destination. Andy is concerned about a live unidentified cable perhaps with loose live ends, hidden under the floor, or in the loft sitting there ready to bite somebody such as a plumber.
Z.
davezawadi (David Stone):
Z, If you contract to do an EICR, you have no permission to do anything else.
That is not necessarily the case David. I normally say to the customer before I start, that I will carry out an electrical inspection and test, it will take approximately x hours, and if I come across any small items that need attention I will attend to them. Consent is then given to me by the customer. I then proceed. Small items may include changing a fuse from a 13 Amp one to a 3 Amp one in a fused connection unit, tightening screws on wiring accessories, supplying and fitting a missing accessory screw, re-fixing an immersion heater flex that has pulled out of its strain relief strap, replacing a cracked/damaged wiring accessory, fitting a blank cover in a consumer unit where there is a hole etc. These are easy to undertake when you have your tools to hand, and it saves the customer money. This is called customer service and is normally much appreciated.
Z.
davezawadi (David Stone):
How many would attempt a full inspection of the insulated loft?
When Mother needed a new boiler, the man from warm front refused to go into the loft, or even open the hatch on the basis that he had to maintain 3-point contact on the ladders all the time. The man who got the contract jumped up there like a frog. (And did a very good job.)
I hate Rockwool and when it's contaminated with rodent droppings and the space is full of spiders' webs, old wasps' and birds' nests, dust, and umpteen old cardboard boxes, I am just not going there!