MHowell:
BOD,
The main fuse, the meter, the henley block and the consumer unit all say 100A on them.
But I don’t think the supply is the issue here. I think the problem is, as mapj1 said, the earthing and the fact that the charger may need an earth rod while the other circuit in the garage uses the earth from the supply.
Ah, now we are getting somewhere. Matey wants a TT earth for the EVCP and the other circuit has a DNO's earth. Presumably both circuits will be within reach of each other, so unacceptable.
Perhaps MHowell would like to tell us where the car will in fact be charged?
MHowell:
The main fuse, the meter, the henley block and the consumer unit all say 100A on them.
perspicacious:
This doesn't necessarily mean that the supply is capable of supporting 100A, just that the individual bits of equipment can. For example a cut-out may say "100A BS 1361", but that just means the maximum fuse it can support. It may well have an 80A fuse it.
What colour is the cut-out? Grey or black?
Regards
BOD
Has the anti-EV brigade taken over this forum?
There's no problem running an EV charger off an 80A supply. Or a 100A supply that can only supply 100A for short periods.