This doesn't necessarily mean that the supply is capable of supporting 100A, just that the individual bits of equipment can. For example a cut-out may say "100A BS 1361", but that just means the maximum fuse it can support. It may well have an 80A fuse it.
What colour is the cut-out? Grey or black?
Regards
BODHas the anti-EV brigade taken over this forum?
There's no problem running an EV charger off an 80A supply. Or a 100A supply that can only supply 100A for short periods.
No disagreement there Simon but I think that in most domestic installations the addition of a charge point rated at 7Kw will push the MD over 60A (using standard load assessment). That being the case, the DNO must be notified PRIOR to installation. With load management, notification can be given to the DNO within 28 days AFTER the install. If you communicate with the DNO in this area, you will be lucky to get a response by next Christmas! Hence it is highly beneficial for contractors to fit load management when the just want to get the job done.
As MapJ has pointed out this only serves the individual property. Things may get tricky for DNOs as EV uptake increases. No doubt that is what the smarts and OCPP is all about.
Has the anti-EV brigade taken over this forum?
There's no problem running an EV charger off an 80A supply. Or a 100A supply that can only supply 100A for short periods.
True. and not anti EV,
But...
someone will need to pay to upsize the transformer after there are more than perhaps the first 6-10 houses per phase of the substation that have EV commuters.
It will become vitally important to understand ADMD (and also DNO cable ratings - see pages 8-13 ) - this is not like adding electric showers that are each on for 15 mins at a time tops.
You may not realise that round here a typical housing estate 500KVA lump will feed ~ 200 single phase properties each with 100A fuse, and most built up areas will be similar. Out of town the pole pigs that feed a couple of farm houses may do better, as the smallest Tx they install these days are either 25kVA or 50KVA split phase, even if only for a couple of properties.
M.
davezawadi (David Stone):
Have you looked at the news from Texas (probably not the Greenest state) that cyclic power cuts have been operating for several days because the wind is not strong and the turbines have frozen up.
According to noted tree-huggers Bloomberg, wind shut downs accounted for only 13% of the energy drop. it was mainly conventional generating stations not being able to cope with the cold weather (instruments freezing up etc):