Geez:
prob a c6 would be better than a b10 considering surge current nuisance tripping (60A vs 50A)
But MCBs are liable to instantaneously trip anywhere within their multiplier range - 3-5x for a B type or 5-10x for a C-type - thus you need to stay below the lower multiplier when you want an MCB not to trip - hence 30A for a B10 (10x3) or 30A for a C6 (6x5).
- Andy.
Chris Pearson:Geez:
They would all comply with a C6 btw. Just wondered if you'd C2 this resulting in an unsatisfactory EICRNow all you have to do is decide whether to recommend replacement with C6 or B10.
Shirley, that is outwith the remit of a report on the condition. ?
Jaymack
under fault conditions ADS has to work to prevent anyone getting an electric shock but what would you code a standard class 2 lighting pendent that had no earth connected? there are no exposed conductive parts on the circuit to get a shock from, the Zs test was made on the unterminated cpc of the T&E cable at the end of the circuit.
Geez:
... but what would you code a standard class 2 lighting pendent that had no earth connected? there are no exposed conductive parts on the circuit to get a shock from ...
This topic came up this afternoon when my self-building chum and I discussed the apparent futility of terminating the CPC in the otherwise empty terminal in a ceiling rose with a standard pendant fitting (2-way, so not looped at the rose). Leaving aside the requirement in Bs 7671 to provide a CPC, there is always the possibility that the fitting may be replaced by a class 1 one.
In answer to the above, if class 2 fitted and CPC terminated correctly => no code; if class 2 fitted and CPC snipped off => C3 (couldn't be worse because no fault to danger); if class 1 fitted and CPC snipped off => C2.