Why don' we use RCD trip times for adiabatic equation
When using adiabatic equation for calculating minimum size of CPC, every example I have seen uses 0.1 second or whatever the disconnect time of the mcb element of the RCBO  or MCB will be.
In a domestic sittuation most circuits are protected by RCD's with a trip time of 40mS with significant fault currents, in this sittuation why don't we use 40mS as T in the adiabatic equation?
  • It is a very well lagged 0,75mm cable that cannot take 11 amps pretty much forever. !!  The adiabatic approximation turns to dust for long time duration, as it assumes the heating is all over so quickly no heat leaves the copper core of the cable. It is often stated to be valid for 5 seconds or less - even this is a horrible kludge, as the time constant depends on the cable size.
    For example,  a chunk of 16mm2 will have a time constant of many tens of seconds, while your 0.75mm2 probably starts to get at least heat into the PVC jacket and on its way off to the outside world, within  a couple of seconds...
    In any case, with 60 odd seconds, you are using  the adiabatic approximation in  a region where it is not the most appropriate method.
    (a 1mm core in PVC insulated T and E or round flex in free air is good for 11A with an eventual 40C rise At the same current, 0.75mm2 will see a temperature rise of  4/3 as much, so about 54 degrees. Assuming a 30C ambient, that is a touch under 85C on cable intended for 70C )
    A quick look at accelerated ageing data suggests you will really have several years at 11A to operate the MCB before the cable is significantly damaged.....
    If you had higher fault currents and trip times of few seconds or less really, then you would want to invoke the adiabatic equation, but by then the MCB has got out of bed, yawned, stretched and is actually reacting pretty promptly.,,,
    Hope this is reassuring.
    PS, for cable, as for fusewire, you can create a composite curve of current versus how fast the ADS must operate, The cable continuous rating forms a vertical line, here in red, as currents at or below that are OK for infinite time duration operation (well decades) . Then as the current goes up, so the permissible duration comes down  - at the very high current end of things,  the times are short, and set by a 'constant energy' situation, here in blue as there is no cooling, In between one can create intermediate points using data like that in the accelerated aging data above, or shown in purple in this graph, the eye of faith...
    These previous discussion threads may help explain that better.
     Adiabatic plots
     Cable Sizing based on I2T - 5 second boundary
    Note that the onset of some cooling is far faster than the final time to reach steady state temperatures - curve below  from (https://electrical.theiet.org/media/1704/establishing-current-ratings-for-cables-in-thermal-insulation.pdf ) suggests tens of minutes. Again, you have ages before anything  gets even slightly near dangerously hot,
  • This would appear to show that a B6 is unable to protect 0.75 sq mm cable unless you can achieve "instantaneous tripping").
    Unless you go down the 435.1 route - In ≥ Iz so overload protection is provided, and as long as the breaking capacity is suitable, fault protection may be assumed.
  • In ≥ Iz so overload protection is provided,
    Yes, with the important caveat being that would only work if there are no de-rating factors to apply to the 0.75 sq mm conductors, because Iz is the current-carrying capacity in the given installation conditions. (Hopefully, the cable is suitable for 6 A in the given conditions in this particular case, but there may well be cases where protection against overload by other means, or where overload protection can legitimately be omitted.)
  • I've lost count of the number of EICRs I've seen where the testers have failed 1mm lighting circuits that are protected by a 16A MCB.
    It would be interesting to see a general justification for 16A MCBs protecting 1.0mm² conductors for faults - 434.5.2 points us to confirming that I²t ≤ k²S². A PVC insulated conductor typically has k=115 so 1mm² has a withstand (k²S²) of 13,225 A²s. Compare that with BS EN 60898's generic values for energy let-through (I²t) for a B16 of 15,000 A²s at 3kA, rising to 35,000 at 6kA (or 18,000 rising to 42,000 for a C16).
    For a B6 (or C6), as In ≤ Iz we can at least use 435.1 to deem it OK (presuming the MCB has the required breaking capacity).
    Some MCB manufacturers publish their own lower figures for energy let-though, which may tip the balance in your favour in specific cases of course, but that's a long way from being able to make a blanket statement of suitability.
  • Indeed, though a lot depends on the type of wiring. For identically sized conductors, table 54.7 can be used to determine suitability without even needing to do an adiabatic. Would be difficult to state that the circuit wasn't compliant, especially if 433.3.1 was applied.
  • For identically sized conductors, table 54.7 can be used to determine suitability without even needing to do an adiabatic.
    Only for c.p.c.s - you still have the problem of proving that a 16A MCB protects the 1.0mm² live conductors against faults.
  • Thanks Graham, I'm still digesting the info and trying to get hold of a copy of BS 7454, but in the meantime I have tried to answer your questions below:
    Agreed - so what is protecting the 0.75 sq mm?
    OCPD: Schrack RCBO C6 30mA, type A, 6kA (backed-up by a 40A BS88-2 fuse)
    Is that specification also requiring you to conform to BS 7671? 0;.75 sq mm is only permitted (Table 52.3) for specific appliances (per the product standard) or in cables with seven or more cores
    Well, these cables are pre-installed in the roadside cabinet, flexible cables with IEC 13 connectors on the end, ready for the specific roadside controllers to be plugged in to them upon installation within the cabinet. In order to confirm the volt drop, EFLI and load within the calculation design software I need to include these, even if there was a get-out clause. I have assumed these cables are as per Table 4F3A for Flexible non-armoured cables. The manufacturer's CCC of 10A certainly matches the table.
    It turns out that the cabinet manufacturer has actually gone one size above the specification and is using 1mm2, which is better but it does not remove the issue. From the advice on here it sounds like I may be able to prove that the proposed scenario will not actually be a problem, however the design calculation software is still going to highlight a problem as it is working off worst case values and probably simplified calculations. But if I can satisfy myself that the scenario referred to in my original post (but with S now being 1mm2) will be compliant I will be happy.
  • Mike, thanks for your responses and for the links to previous topics.
    I will look to prove that the situation will be ok using these suggested alternative methods, and use that to supplement the design software that appears to still be using the Adiabatic for a 400+ second fault.
  • however the design calculation software is still going to highlight a problem as it is working off worst case values and probably simplified calculations. But if I can satisfy myself that the scenario referred to in my original post (but with S now being 1mm2) will be compliant I will be happy.
    Agreed ... there are limitations to software that the experienced designer needs to use their experience to handle (and.or select the appropriate parameters or course of action).
    0.75 sq mm can carry up to 10 A, but only under certain conditions - one of those being the length is limited to < 2 m, when used to supply appliances from a standard circuit to BS 7671 (for example, see Table 2 to BS 1363-1) which is roughly what you're describing here.