Air source Heat Pumps and Diverted neutral currents
Hi I have been having a conversation around the requirements to fit an RCD on these circuits, it turns out it is a manufactures or appliance standard recommendation. It then occurred to me what out diverted neutral currents if the protective earth & neutral conductor (PEN) were to break.
If these units are fitted on a TN-C-S earthing system and the PEN conductor breaks the metal casing could become live as the earth conductor could end up carrying the neutral current.
The person touching the ground would be earthed and the current would flow through them, in this case an RCD would not function as it wouldn’t see the imbalance. I feel it should be considered its no different to having an electric vehicle charger and having a metal car. For that an Open PEN detection device is required.
Any thoughts on this point ?
Daniel
  • Any thoughts on this point ?
    Until EVs were invented, nobody even thought of Open PEN detectors.  Everybody worked on the basis that if it was on an RCD, it was fine.  Loads of metallic things are used outside.  Lawnmowers, cement mixers, outside lights, etc.  But our homes aren't surrounded by piles of dead bodies.
  • Agreed.
    There is also a clue inasmuch as the electrics will have stopped working.
    I suspect that isolated loss of PEN is very rare save for aerial supplies in singles. Last night's storm may be another clue.
  • But, (but!)  since about 1970, all lawnmowers hedge trimmers etc - essentially all hand held outdoor appliances, have been Class II - that is to say double insulated, for exactly this reason - so you are not relying on a CPC that may not be at terra-firma earth potential.
    Fixed equipment, like lampposts and bus shelters provide their own electrodes from the foundations, or for some comms equipment  (and lighting in phone boxes, oddly) are wired as TT so as not to use the TNC-s earth.
    outside lights on a house dont generally get held onto
    Things with an unavoidable earthed metal nature (Caravans and boats come to mind, and some farm equipment like semi-enclosed milking parlours ) are prohibited from using the TNC-s earth, and must be TT.
    EV cars are the odd one out, in that the TNC-s supply was already there.
  • I feel it should be considered its no different to having an electric vehicle charger and having a metal car.
    As with anything, there are pros and cons. EV's aren't the only "Class I" item outdoors - think street lighting, domestic outside lights, external boilers, metal framed/clad buildings, those green boxes at the side of the road, and of course non electrical equipment bonded to the PME terminal - gas pipework, and outside taps. Unlike EVs there's no demand for open-PEN detection on any of those.
    One of the big considerations is how likely is someone to touch the thing during an open-PEN event - an EV is very likely to be grabbed hold of several times a day (not least when connecting/disconnecting) - but when was the last time you actually touched a lamppost when you walked past one?
    Add in that some of the means of protection can increase other risks - e.g. changing to TT increases the risk of earth faults remaining connected due to a faulty RCD - open PEN devices put a moving contact in the PE - so increasing the changes of a failure of basic earthing (and the common types don't necessarily spot all dangerous situations anyway). Some methods - e.g. introducing an insulating section in pipework or supplementary electrodes are generally lower risk and are often recommended, but have limited application.
    So often it's less of a case of "identifying a risk and eliminating it" but rather balancing one risk against another.
  • EV cars are the odd one out, in that the TNC-s supply was already there.
    Also, whilst a heat-pump might be supported by a metal frame, which might be on or in the ground, an EV sits on four large black insulators.
  • Addendum...
    if you want to know how rare or not a lost neutral event is, consider page 16 of this report.
    Where figures for different UK DNOs imply something between  7.96 x 10 -4 and 3.68 x 10 -4  chance per year per household of a neutral fault 12 years ago.
    PS I have experienced one, and am aware of another.
  • whilst a heat-pump might be supported by a metal frame, which might be on or in the ground,
    Heat pumps typically also sit on rubber supports (to mitigate noise/vibration) - either directly on large rubber "skids" or on four smaller feet between the HP and the supporting frame.
  • Thank you every one for your input, its one of those things that you think but what about that. Hopefully air source heat pumps might get a special location listing in BS7671, so we have more guidance on these installations. Still relatively new to the industry at present. So in your comments basically saying don't worry about it.
    I thought the latest figures for broken PEN faults was around 500 a year. Hence why the IET set up a webpage so you can report it, to enable figures to be collated.
  • A few years ago a neighbour called me to ask if the electricity was off as nothing was working. A few quick tests showed he had no neutral and as far as I could see it was the recently connected smart meter where the neutral was lost. A call to SPEN emergency number and they came out quickly and found the neural connection in the smart meter was loose. The neighbours energy supplier would not talk to the SPEN engineer as he was not the customer so it never got reported. I wrote a couple of letters for the neighbour to the energy supplier CEO which resulted in a £50 refund for him.
    Speaking to a SPEN manager a year later he said it should have been reported and the installer put under supervision and other installs checked.
  • the neural connection in the smart meter was loose.
    Certainly not good (a fire risk if nothing else) but at least in the UK that would certainly be after the N-PE split in the cut-out, so at least the earthing system didn't become hazardous live, as can happen with a true PEN fault.