As each (RCD) Residual Current Device must not have more than 30% leakage current on it.
It's hard to see how dual (RCD) Residual Current Device boards can be fitted at all these days.
i come across so many dual rcd boards with solar, evse and heat pumps on them, these have all been recently installed.
i wonder if BS7671 should state: Dual (RCD) Residual Current Device boards shall not be fitted, unless it can be shown (and documented) that they are suitable for the combined leakage currents expected .
otherwise developers will keep specifying them and i will have keep educating them on the many reasons a type A rcd should not be shared with other equipment!.
maybe manuafactuers instructions should also state : not suitable for a shared rcd, for certain equipment.
Parents
  • Three days ago I said:

    ”The question that Graham asked was quite specific:

    ”However, if the lamp is damaged, and the user is being protected against accidental contact with live parts, say after the rectifier, would the type AC RCD operate is perhaps another?”

    in that he said “after the rectifier”, so assume there are some diodes charging a capacitor, which discharges to supply the DC current, and the input current is 25 mA at 230 volts, what is the DC output current and voltage?”.

    So presumably after the rectifier the current and voltage is peak, not RMS? So if the current and voltage is 25 mA at 230 volts AC measured RMS, then after the rectifier it should be 35,35 mA at 325 volts pulsed DC unless there are a few more electronic components to drop the voltage?

  • it is d.c. It does not have to be smooth.

    hmm..

    Would you consider a unipolar square wave, or a triangle wave where the lower crest is at zero, as examples of DC?

    I would not, because in addition to a DC term (0Hz, non changing, there for 'ever' or at least for the duration of the measurement) , there is a clear fundamental frequency, and some harmonics...

    I agree there is a de-minimis case where the 0Hz term dominates - a DC with a bit of ripple on it is a common situation and makes sense described as such.

    I might even consider the output of a 3 phase bridge to be in that class, but I'm not sure I'd consider something that fell to zero for a non-trivial part of the time to be quite the same.

    I'm not sure how well that fits with the more 'power electrical' definitions, it is certainly open to more than one interpretation.

    Mike

  • Perhaps we should re-introduce the term "continuous current"....

       - Andy.

  • Would you consider a unipolar square wave, or a triangle wave where the lower crest is at zero, as examples of DC?

    I think that I can see Mike's point. Whilst square-wave d.c. might be useful, e.g., for a flashing lamp, I suspect that the usual aim is to obtain smooth d.c.

  • Save that, for example, your 42 mA half-wave rectified d,c, superimposed upon 6 mA of smooth d.c. would be continuous.

    Here is a Boxing Day question for all of you. It may be unlikely to occur, but if you had one device on a circuit with a fault to ground of 15 mA r.m.s. a.c. and another one with a fault of 15 mA r.m.s. half-wave rectified pulsating d.c., would a 30 mA type A RCD trip?

  • We need to take care with the peak, average (mean) and rms values of such signals.

    The 'pi' value keeps cropping up in a lot of situations (e.g. see also noise bandwidth vs signal bandwidth factors).

    As an aside, what is truly missing, is the explanation as to how/when these half sine [pulsed DC] style currents actually 'blind' the RCD. The pragmatic engineering/ material/physics are just (if not more) interesting than the mad/bad maths definitions Smiley.

  • ... re-introduce the term "continuous current"....

    maybe we should, but I think we'd have to agree what we meant by it first, which is kind of where we came in.  If we assign a single figure to something that is changing, are we refferring to  its mean, its RMS or its peak ?

    I'm not sure..

    Mike

  • fault to ground of 15 mA r.m.s. a.c. and another one with a fault of 15 mA r.m.s. half-wave rectified pulsating d.c., would a 30 mA type A RCD trip?

    haha - maybe only  half the time ;-) 

    you have defined exactly what you want, The sum of these upper 2 current traces, making the lower one

    We do not, however, as we have just discussed,  know for certain what the RCD spec actually means.

    Mike

    PS for those interested, this is a simulation in LTspice, a tool I find helpful for this sort of stuff.

    This is the circuit being simulated.

  • haha - maybe only  half the time ;-) 

    Mostly not, IMHO.

    If my maths are correct, the RMS value of the combined current is only 16.8 mA.

    But is, "mostly not" (or 50% of the time) a single RCD being exposed to an imbalance many times, or many RCDs being exposed only once?

    If we assign a single figure to something that is changing, are we refferring to  its mean, its RMS or its peak ?
    We need to take care with the peak, average (mean) and rms values of such signals.

    I think that we are all agreed on that. :-)

    P.S. this discussion beats the dross on the telly by a country mile.

  • I have added the RMS calculations to the simulation above (and updated the screenshot image in the post above, to reflect that just in case someone else wants to know how to try this sort of thing at home ) and the combined RMS is not as low as you might think, coming in at almost exactly  27mA. - it is not simple power addition (which would be root of sum of squares - think Pythagoras) because they are synchronous functions, - that is to say the peaks of the rectified and un-rectified waveforms are always aligned, and  not independent of each other and those peaks, while only there half the time, count for most of the RMS energy.

    The spice log is as follows.

      

    I appreciate that there are quantisation errors, so the nominal 15mA RMS in the 2 limbs is not quite, but this still illustrates the point

    It may help to visualise this by considering the power as a function of time, rather than smoothed over many cycles,

    regards 

    Mike.

    PS schematic edited to create named nodes r1 and r2 so that we can plot the current in the component times the voltage across it with a meaningful name.

  • you appear to be thinking of the average current,

    very true, indeed I am, my mistake and while embarrassing it sort of reinforces the  point that it is important to be clear about these things, and easy to be confused ! Oops.

    Mike.

    PS missed this post at first as the website had carefully folded it away...  

Reply
  • you appear to be thinking of the average current,

    very true, indeed I am, my mistake and while embarrassing it sort of reinforces the  point that it is important to be clear about these things, and easy to be confused ! Oops.

    Mike.

    PS missed this post at first as the website had carefully folded it away...  

Children
  • The other "problem" is that we generally don't have a good handle on the magnetics that cause the perceived 'average dc' to create the blinding effect.

    I've long thought it's probably a combination of the ferrite ring/core's saturation and hysteresis that shifts the operating point of the putative 'difference current transformer' to a point that has a low effective turns ratio (which would mean the trip solenoid would not activate at the expected [AC] leakage current).

    The saturation & hysteresis are determined by the specific material / ferrite in the particular RCD / GFCI brands. so likely to be highly variable as to test outcome for our general test of a random spare RCD from the disposal pile [I've recently pulled apart an old BG CUR8030 to try and see what is really in there]

    Average DC may not be the [pure] problem.

    Found https://physics.stackexchange.com/questions/60194/equation-describing-magnetic-hysteresis as a description of the equations for the magnetics. Yet to study it.

  • easy to be confused ! Oops
    derivation by integration is left to the student

    I too confused myself. When adding full-fat and semi-skimmed currents, I forgot to take into account that the relationship between RMS and peak values is different, and accordingly, the equations of the sine waves are different.

    I now have 15 + 15 ≈ 27.7, which agrees with Mike's value, subject to "quantisation errors".

    I have re-done my algebra and find:

    So where both components are 15 mA, the total is √(2 + √2) x 15 mA ≈ 27.7 mA

  • That is a reassuring result, and yes, pythagoras plus the cross term that makes all the difference looks right to me. I'll allow the 700micro-amps as the sort of thing that LT spice does not get right when it does its 'join the dots' integrations rather than  the pure maths. I will own up to being very good at losing factors of pi, 1/e and so on, when I do algebra under pressure and therefore I often use numerical tools like LTspice and others as a means to get close enough, when perhaps I should be reaching for a pen and thinking more.

    Now, if only it was as simple as the RCD tripping on any repetitive waveform with the correct RMS value, then a device designed to trip at some point below 30mA on a sine wave probably would on this too. However, as noted in the other post, the physics conspire to make it very hard to say much with any certainty at all beyond ' it'll need to be experimentally determined'. I think here transformer core saturation is more important than hysteresis, but that is probably one of the most material dependent parameters. 

    I don't have a reliable set of saturation models for anything beyond the simplest representation of materials, and worse, while some pretty complex models exist, (Wolfarth, Stoner, 1940s, and Jiles- Atherton in the 1990s) I'm not sure that anyone really has one that is a good fit to reality for generic real materials over a wide range of conditions.

    LT spice does include a modified Chan model, as per this patent, https://patents.google.com/patent/US7502723 and certainly can be used to show saturation-like  trends that look more or less correct, but I'm not sure I'd want to design anything critical with it.

    Mike

  • Now, if only it was as simple as the RCD tripping on any repetitive waveform with the correct RMS value, then a device designed to trip at some point below 30mA on a sine wave probably would on this too. However, as noted in the other post, the physics conspire to make it very hard to say much with any certainty at all beyond ' it'll need to be experimentally determined'. I think here transformer core saturation is more important than hysteresis, but that is probably one of the most material dependent parameters.

    Nicely put. :-)

    I can imagine an expert in court being examined by counsel: "Which part of the wave is not sinusoidal?" What would you say?

    Here we have slightly more at 16.25 mA  a.c. + 16.25 mA d.c. because the combined RMS is 30 mA. So, I thought let's get as close as possible with pure a.c. Problem is that the average current > 0, so it is necessary to add a little smooth d.c.

    The graphs look pretty similar to me, but would either (or both) trip an RCD?

  • In my disassembled old unit there is a rectifier diode after the sense toroid which may be aligned with the trip solenoid's magnetic latch.

    If it requires a negative going current then ?? .. need to see how the material hysteresis curve is biased, and internal circuit responses ? 