I suspect you're not going to get a nice yes/no answer for this - as there's no clear definition of what makes such a system safe or unsafe in the first place.
As a bit of background there was a thread about the way open-pen devices like this work - Open PEN detection for 722.411.4.1 (iv) - as you seen there are situations where the results are perhaps less than ideal anyway. Increasing the acceptable voltage range will increasing the probability of the system remaining connected in a hazardous situation, but given the original system is not entirely perfect in the first place, whether that constitutes a significant reduction in safety is debatable rather than calculable.
I could see an argument that if the device had some additional mechanism for reducing the risk from shock under broken PEN conditions - not just voltage measuring, but say monitoring the c.p.c. current and disconnecting immediately if hazardous shock levels were present (say >10mA), and as that wasn't compromised at all by the voltage limit change, the overall risk might not be significantly increased.
- Andy.
Might be worth renting a CA PEL (Chauvin Arnoux Power and Energy Logger) to collect some data as to the lows and highs. Other brand are available. I suspect as time goes on this will become more regular as sites change from Consumers to ProSumers. In the north of England people are stating that they are regularly getting 250 to 253v. This is probably why the EVSE (Electric Vehicle Supply Equipment) manufactured has the ability to tweak the tolerance to 256v.
Things will start to play different at 256v think about ADS (Automatic Disconnection of Supply) will it now become to sensative or not respond quick enough. This will probably need the IET, ENA (Energy Network Association) and EVSE industry for the UK to sit down and discuss this further.
Thank you very much for this Andy - and I would agree with you that there is no simple yes or no answer here. I am in a difficult posistion due to the fact we have manufacturers stating that voltages can be increased while myself as the installer is left scrambling to understand the comlexities of this decision.
I really feel at a lost at present, the charger I am discussing does have additional monitoring on the CPC so that is a benefit, I am still unsure how I can justify that in terms of upping the voltages - against what is in BS7671? Would you have any thought or comment on that?
Hi Serigio, the company I work for has bought one of the voltage units you have mentioned, we have used that for volatge monitoring to compare data ion our back office with our OCPP logs in order to provide factual data to DNOs. In a way trying to prove that we are not wasting their time so to speak.
Thanks for this Sergio, really appreciated.
I see that in New Zealand the have changed their supply voltage limits because of Prosumer issues from +6% to +10%, while keeping the DNO supply level at +6% to allow for back feeding from solar on longer distribution lines.
see https://www.youtube.com/watch?v=s8RXQERPzMY "The newly announced NZ Grid Voltage Increase explained".
This may give one view on how to explain things, even if it's not directly equivalent.
The other option is to distinguish between a "Fault" and "Disturbance" (aka Dangerous vs Annoying).
Thank you very much Philip, I will have a look at that video.