I suspect you're not going to get a nice yes/no answer for this - as there's no clear definition of what makes such a system safe or unsafe in the first place.
As a bit of background there was a thread about the way open-pen devices like this work - Open PEN detection for 722.411.4.1 (iv) - as you seen there are situations where the results are perhaps less than ideal anyway. Increasing the acceptable voltage range will increasing the probability of the system remaining connected in a hazardous situation, but given the original system is not entirely perfect in the first place, whether that constitutes a significant reduction in safety is debatable rather than calculable.
I could see an argument that if the device had some additional mechanism for reducing the risk from shock under broken PEN conditions - not just voltage measuring, but say monitoring the c.p.c. current and disconnecting immediately if hazardous shock levels were present (say >10mA), and as that wasn't compromised at all by the voltage limit change, the overall risk might not be significantly increased.
- Andy.
I suspect you're not going to get a nice yes/no answer for this - as there's no clear definition of what makes such a system safe or unsafe in the first place.
As a bit of background there was a thread about the way open-pen devices like this work - Open PEN detection for 722.411.4.1 (iv) - as you seen there are situations where the results are perhaps less than ideal anyway. Increasing the acceptable voltage range will increasing the probability of the system remaining connected in a hazardous situation, but given the original system is not entirely perfect in the first place, whether that constitutes a significant reduction in safety is debatable rather than calculable.
I could see an argument that if the device had some additional mechanism for reducing the risk from shock under broken PEN conditions - not just voltage measuring, but say monitoring the c.p.c. current and disconnecting immediately if hazardous shock levels were present (say >10mA), and as that wasn't compromised at all by the voltage limit change, the overall risk might not be significantly increased.
- Andy.
Thank you very much for this Andy - and I would agree with you that there is no simple yes or no answer here. I am in a difficult posistion due to the fact we have manufacturers stating that voltages can be increased while myself as the installer is left scrambling to understand the comlexities of this decision.
I really feel at a lost at present, the charger I am discussing does have additional monitoring on the CPC so that is a benefit, I am still unsure how I can justify that in terms of upping the voltages - against what is in BS7671? Would you have any thought or comment on that?
I see that in New Zealand the have changed their supply voltage limits because of Prosumer issues from +6% to +10%, while keeping the DNO supply level at +6% to allow for back feeding from solar on longer distribution lines.
see https://www.youtube.com/watch?v=s8RXQERPzMY "The newly announced NZ Grid Voltage Increase explained".
This may give one view on how to explain things, even if it's not directly equivalent.
The other option is to distinguish between a "Fault" and "Disturbance" (aka Dangerous vs Annoying).
Thank you very much Philip, I will have a look at that video.