AJJewsbury:
Similarly there are margins built into overcurrent protective devices - e.g. an MCB shouldn't trip when carrying current 13% above its rating (at least not for conventional time - usually an hour), Likewise cables would be expected to carry those sorts of currents above their ratings for such periods without significant damage (otherwise our whole approach to overload protection - In ≤ Iz falls apart). So it would be logical for the same to apply to accessories such as plugs and sockets (unless their product standards say otherwise).
On that basis, we would ignore BS1363 and go by the characteristics of BS1362 fuses. If it doesn't blow the fuse, it must be safe! ?
Incidentally, I have (moulded on) 13 A plugs which are rated at 3 A or 5 A.
ebee:
Mapj1,
ref " N-E reversal at the plug, a mistake that RCDs have almost eliminated."
Could you elaborate on that please? I`m findinding difficulty grasping the reason.
Thanks
Because the load would then be connected L-PE rather than L-N so the RCD would see all the normal load as leakage and trip (unless it was a particularly small load - well below 6.9W).