perspicacious:
if the 20 A DP switch supplies only a single socket-outlet, surely overload current protection is not necessary as per 433.3.1 (ii).
Simply, are the INPUT/loop in terminals of a 20 A DP switch suitable for connection to a 32 A RFC irrespective of whatever is on the OUT terminals?
Regards
BOD
This is the same question re Wago's ? Provided the terminals are sized for either 2x2.5 sq mm or 2x4 sq mm, surely there's not an issue here?
And ...
Does the 20 A DP switch need to be protected by a B20, C20 or D20 ... can it be protected by a B25? or B32 provided the load determines overload protection is not necessary? Imagine I have a machine with B20 breakers on the input, and I supply it from C25 or B32, is this OK to go through a 20 A DP switch or would I need a 25 A or 32 A DP switch ?
Let's not get fault protection ("adiabatic"), and ADS (meet a disconnection time for safety), confused with protection against overload current.
ebee:
Just a note about the 3 x 2.5 conductors - a 4.0 radial strictly does not facilitate a 2.5 spur adding by the standard but it is encouraged in the guidance
It's also fair to say that the terminal performance in BS 1363 is a minimum requirement, a manufacturer may make their terminals suitable for other configurations that exceed BS 1363 requirements.
perspicacious:
This is the same question re Wago's ? Provided the terminals are sized for either 2x2.5 sq mm or 2x4 sq mm, surely there's not an issue here?
Until that is answered, there's no point in adding further asides unless a career in politics is looming?
Again, simply, are the INPUT/loop in terminals of a 20 A DP switch suitable for connection to a 32 A RFC irrespective of whatever is on the OUT terminals?
Regards
BOD
Provided the manufacturer's information shows that the conductor sizes for the terminals are suitable for 2 x 2.5 or 2x 4 sq mm, I don't believe there's a problem. Many of them are suitable for the same conductor configurations as BS 1363 accessories.
Is there any reason to conclude otherwise?
So, I checked - BS EN 60669-1 is being used for switches now, not the general standard BS 5733.
20 A switches are tested for temperature rise with a current of 25 A, which is broadly in line with the tests for BS 1363 accessories.
perspicacious:
Wago 773-104
Max 2,5 cable
Terminal current rating 24 A
However, Table 4D5 Method C for 2.5 cable gives 27 A
27 A > 24 A
Regards
BOD
Your point, I'm guessing, is that 773's are not always suitable for all circuits with 2.5 sq mm cables ... but that still doesn't answer RFC's.
For 2.5/1.5 cable, Reference Methods 100, 102, A and C are permitted for 32 A mcb/RCBO, or 32 A BS 88-2 or 88-3 fuses.
From 4D5 for 2.5, Reference Methods 100 and 102 are only 21 A, and Reference Method A is only 20 A !
So is the 773 suitable for RFC's?
perspicacious:
Provided the manufacturer's information shows that the conductor sizes for the terminals are suitable for 2 x 2.5 or 2x 4 sq mm, I don't believe there's a problem. Many of them are suitable for the same conductor configurations as BS 1363 accessories.
Is there any reason to conclude otherwise?
Conclude as opposed to assume? When I contacted several manufacturers years ago asking if their 20 A DP switch input terminals were suitable for connection to a 32 A RFC, of the few that re[plied, their only comment was that the switch was made to BS 5733.
Regards
BOD
Hopefully, then BS EN 60669-1 will sort that out then, per earlier post?
I agree, it's not made easy. The response you received was far from helpful.