EICR - main earth and neutral

Former Community Member
Former Community Member
Hi was conducting a EICR on a consumer unit today removed the cover and Main earth cable was 8 x single strand insulated cables istead of expected single 25mm also earth was the same??? it is in an apartment and has been running fine for

at least 20 years, just want to know what to input for csa?? and should I note it in observations under C3 CODE???? ANY ADVISE WELCOME THANKS
  • Sparkingchip:
    davezawadi (David Stone):

    Another example. Now discuss if this is permitted because I won't.




    You have already discussed it and the answer isn’t clear cut.

    https://communities.theiet.org/discussions/viewtopic/1037/25616


    I asked where the meter is with the intention of trying to determine if the cable should be classified as suppliers equipment or part of the consumers installation, the next question is what fuses are installed to protect this cable, is protected by the suppliers fuse or a fuse within the consumers installation?




    It depends on whether the cable is owned by the BNO or the consumer - quite possibly the BNO in which case effectively not the consumer's equipment.


  • One end of this cable has to connected to a meter, I would like to see how this has been done.


    The manufacturer’s state on their data sheets that the neutrals are coated with a polymeric compound and I am not convinced that is true insulation.


    If the cable insulation is tested at 500 Vdc will it pass?
  • gkenyon:


    It's entirely possible (and perhaps more likely) that a line to neutral or line to earth fault will only short line to a single strand of the neutral or earth (or perhaps a few strands).

     



    A highly likely scenario is that a carpenter fires a nail from a nail gun into a concealed cable, it would almost certainly only contact two of the neutral conductors and the whole of the live conductor, bear in mind there’s possibly nineteen neutral conductors so that gives an effective neutral of say 2.6 mm.


    Which melts first, part of the neutral conductor, the nail or the fuse and what happens whilst one of them blows to clear the fault?

    https://www.elandcables.com/cables/concentric-and-split-concentric-cables
  • davezawadi (David Stone):

    Another example. Now discuss if this is permitted because I won't.


     


    No, not on the consumers side. Yes on the DNO side. ?


  • It depends on how good the “insulation” on the neutrals really is.
  • Sparkingchip:
    gkenyon:


    It's entirely possible (and perhaps more likely) that a line to neutral or line to earth fault will only short line to a single strand of the neutral or earth (or perhaps a few strands).

     



    A highly likely scenario is that a carpenter fires a nail from a nail gun into a concealed cable, it would almost certainly only contact two of the neutral conductors and the whole of the live conductor, bear in mind there’s possibly nineteen neutral conductors so that gives an effective neutral of say 2.6 mm.

     


    Agreed - and yes, it depends on the makeup as to the actual number and csa of the N conductors. Sounds like possibly 35 sq mm rather than the 25 sq mm example I ran through?


  • Which page of BS7671 permits split con on the consumer's side of the meter, or under BS7671 at all? It is probably not dangerous but is not protected, the sheath does not provide much mechanical protection to the very weak N insulation, terminating the centre aluminium conductor may be difficult because of corrosion/bimettalic consideration etc. I can find no reference to BS7870 in BS7671.
  • David


    Commonly used on BNO installations from the Ryfield board to a series 8 Head fitted with a solid link red head for meter isolation. Surface run cables only for the unmetered supply to a local cut out with a red head solid link with the neutral and earth separated. It is still TN-C-S on the incoming supply cable but the neutral and earth split on the BNO network to comply with BS 7671.










  • davezawadi (David Stone):

    Which page of BS7671 permits split con on the consumer's side of the meter, or under BS7671 at all? It is probably not dangerous but is not protected, the sheath does not provide much mechanical protection to the very weak N insulation, terminating the centre aluminium conductor may be difficult because of corrosion/bimettalic consideration etc. I can find no reference to BS7870 in BS7671.


    Chapter 52 does not mandate any particular list of standards for cables. Not all possible cable types are listed in BS 7671 - and even the tables that are provided don't have enough information to fully design with all of the cable types listed (e.g. armour CSA for SWA types, unusual installation methods such as sheathed cables in conduit, etc.).


    At least this has a British Standard for the cable construction, so there should be no issue there ... provided it meets CPR fire performance requirements ?


    So, provided it's deemed to meet the external influences requirements (some examples you've stated, perhaps), there should be no problem ... but as John says this may be BNO and outside the scope of BS 7671 as it's possibly distributor's equipment ?


  • BNO - the unicorn like Building Network Operator, which may just be a slightly bemused freeholder and his/her tame sparks, should be working to BS7671. The DNO stuff stops in the basement at the company fuses.


    In a typical block owened by a freeholder but with a few leasehold flats within, anything between there and the flats meters, i.e. riser cables, laterals sub-mains and red links is considered to be 'building network' these days. Still has to be secure against abstraction, but often the maintenance of it is a responsibility void until something goes wrong.

    Often done in split con, sometimes by DNO originally, and then adopted. Newer flats and conversion are more likely to be SWA, or at the small development shallow end just 10mm2 T and E, though to be fair T and E  is more likely with centrally located metering, so the meters are not in the flats, but in some awkward  common cupboard or  basement and they have flat numbers and rude messages telling you what will happen if you turn off the isolator for flat 13  written on them in sharpie pen..



    Mike.