I am inheriting an existing design to review (the installation has been completed for a number of years).
The installation is fed from a main supply "Supply A (from Sub A) and supply A N-E link is in the upstream LV substation.
The installation has a server room with a critical distribution board, the critical DB is fed from an automatic transfer switch
- The ATS is fed by two supplies
- One supply to the ATS is derived from Supply A
- The other supply to the ATS is derived from another supply "Supply B (from Sub B)"
- Supply B N-E link is in the upstream LV substation.
- The neutrals of supply A and supply B are connected together in the ATS
- The ATS changeover switch uses 3 pole breakers (neutrals are not switched)
- Inside the server room there is a mix of 1) Equipment supplied by supply A non critical and 2) Equipment supplied by supply B critical
- The ATS appears to have 4 pole changeover switches but only 3 of the poles are used (neutral not switched)
Please see attached sketch for the five wire diagrams
To my mind there is a lot to be desired about this but I want to double check my thinking by running it past the community:
- Two N-E links present
- Neutrals linked inside the installation
- Not all exposed conductive parts connected to the same earthing system (supply A and supply B)?
- Circulating currents and voltage disturbance
- Stray neutral currents flowing to earth
- Issues with protection
- Etc.
What are your thoughts?
Thanks
Richard